View Full Version : wiring....
inline 6
11-19-2009, 02:26 PM
getting ready to add outdoor lighting. I am putting up 8, fixtures with 50w bulbs in each. I want to add a breaker and switch just for this. I know how to do the wiring. My question is what gauge or spec of wire should I use? Is there a formula for this kind of thing?
93smokinsnakeSVT
11-19-2009, 03:09 PM
20 amp breaker with 14 guage wire should be perfect for that
slyhog22056
11-20-2009, 12:03 AM
How many 50 watt bulbs in each fixture????
Current = power (Watts) / Voltage (120 or 240)
www.sengpielaudio.com/calculator-ohm.htm
RuStYpNuS
11-20-2009, 08:41 PM
20 amp breaker with 14 guage wire should be perfect for that
LOL wrong sir
pm me for more info
15a - 14/2 romex Max Ampacity Rating
20a - 12/2 romex Max Ampacity Rating
50w x 8 = 400w/120v= 3.3 amps
15a circuit and 14/2 would be perfect. If by chance your going to be exposing any of the wire then buy 14/2 UF cable as its uv resistant and weatherproof.
inline 6
11-20-2009, 10:30 PM
LOL wrong sir
pm me for more info
15a - 14/2 romex Max Ampacity Rating
20a - 12/2 romex Max Ampacity Rating
50w x 8 = 400w/120v= 3.3 amps
15a circuit and 14/2 would be perfect. If by chance your going to be exposing any of the wire then buy 14/2 UF cable as its uv resistant and weatherproof.
Ok, so a 15a breaker is ok. I already have a roll of 12/2 outdoor rated. Will this be ok?
RuStYpNuS
11-21-2009, 11:27 AM
12/2 is fine. you just never want to put a bigger breaker on a wire thats not rated to handle the max ampacity of the breaker
here is a useful chart
http://www.cerrowire.com/default.aspx?id=46
vBulletin® v3.8.1, Copyright ©2000-2010, Jelsoft Enterprises Ltd.